Love the EV logo. This is something to tell your friends, if you hire an electrician installs the outlet, make sure it has the EV logo.
That, too, is currently in a state of confusion/transition.

There is currently no requirement to mark a receptacle with an EV logo nor is there a standard symbol for this purpose.

The first receptacle manufacturer I was aware of that marked certain receptacles with an EV logo was Hubbell and their other brand, Bryant.

The logo was a running change. No other changes were made, so the absence of such a logo doesn't mean the receptacle isn't suitable for the task.

There is also nothing preventing a manufacturer of a low-end receptacle from also printing an EV logo on their product.

Eventually, this may change as property damage, injuries, and deaths continue, but for now, even "$10 Leviton" receptacles are legal for EV charging and provided they are properly installed, the installer cannot be held liable for knowingly and willing choosing a $10 Leviton over a $100 Hubbell.
 
I choose to have a hard-wired charger, no plug. The one I choose is Emporia which gives options of plug or hard-wire (hardwire whip). They have phone apps and it works with their energy monitor systems for the house.
Emporia Level 2 EV Charger | NACS (Tesla) or CCS (J1772) – Emporia Energy
Those were $180 on AMAZON/$190 if UL approved when they first appeared and they sold out in hours.
I opened up the instructions and it didn't look easy to me to hardwire, but was a breeze to our Electrician.
Astounding how fast he knocked it out.
Image
 
Some areas require a disconnect within sight of the wall unit. And unfortunately the electrician picks out a disconnect for the outdoor unit of an AC. Which is not designed for continuous duty of an EV. A switch blade disconnect is though.

KOT
Incorrect. Almost all jurisdictions in the US follow the NEC which requires a disconnect only if the equipment is more than 150V to ground (a 240V circuit is only 120V to ground), or if the equipment is over 60 amps (the Gen 3 Tesla Wall Connectors have a limit of 60 amps). In other words, you do not need a disconnect within sight of the Wall Connector. That's just false.

However, a NEMA 14-50 outlet does require a much more expensive GFCI breaker, one more copper wire all the way to the breaker panel and, if the NEMA 14-50 outlet is flush mounted, it's more difficult to install than a Wall Connector. Even if it's not flush mounted it's more difficult and more expensive to install due to the useless extra wire required (not even the Mobile Connector connects to this orphan wire) and the connections on a NEMA-14-50 outlet are never as easy to secure as those in a Wall Connector (which is specifically engineered and built to make easy connections designed for continuous duty).

To some previous posters who pointed out they couldn't install a hard wired EVSE for whatever reason, yes, there are use cases where a Mobile Connector comes in handy. My surprise is the number of people who install a NEMA 14-50 instead of a Wall Connector. In most cases it's sub-optimal reasoning that gets them there. Don't be penny wise and pound foolish!
 
There is still a small number number of states where this is not required since the GFCI for 14-50s didn't start until NEC 2020. :)
Oh sweet, Pennsylvania is one of them. So my installation is code-compliant! :p
 